Observing the traffic on the bus we can see there are different units. These are the address found on the 12 bus : 
4 21 Alessio Valeri
5 71 Alessio Valeri
|ADDRESS|UNIT |
6
|--|--|
7 72 Alessio Valeri
| 41 | Hi-Mit remote controller  |
8 1 Alessio Valeri
| 47 | Hi-Mit remote controller |
9 220 Alessio Valeri
| 50 | Indoor Unit |
10 151 Alessio Valeri
| 57 | Hi-Mit remote controller |
11 1 Alessio Valeri
| 63 | Hi-Mit remote controller |
12 150 Alessio Valeri
| 34 |  |
13 220 Alessio Valeri
| 35 | Outodoor Unit |
14 219 Alessio Valeri
| 146 | Indoor Unit |
15 150 Alessio Valeri
| 242 |  |
16
| 243 |  |
17
18 51 Alessio Valeri
# REQUESTS / REPLIES ANALYSIS
19 52 Alessio Valeri
 Here I try to report any communication pattern I can find :
20 1 Alessio Valeri
21 67 Alessio Valeri
## 41 - 146 interaction
22
Messages exchanged between Hi-mit interface and outdoor unit
23
WIP
24
25 271 Alessio Valeri
#### Status update request
26 296 Alessio Valeri
Every 60s there is a status update request from 41. The request is acknowledged and replied to from 146.
27 271 Alessio Valeri
28
|41|0|9|202|161|9|1|97|11|
29 273 Alessio Valeri
<span style="color:green">ACK from 146</span>
30 271 Alessio Valeri
|146|0|48|9|1|9|0|97|62|0|8|1|6|12|45|28|0|0|0|24|28|28|28|28|28|28|28|0|0|0|0|224|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|184|
31 273 Alessio Valeri
<span style="color:green">ACK from 41</span>
32 271 Alessio Valeri
33 52 Alessio Valeri
## 47 - 242 interaction
34 60 Alessio Valeri
<span style="color:darkorange">|47|0|10|202|160|1|1|108|0|12|</span>
35 52 Alessio Valeri
<span style="color:green">ACK from 242</span>
36
|242|0|48|1|1|1|1|108|62|0|31|129|129|27|0|0|0|0|0|0|0|22|0|0|0|0|0|0|0|20|60|50|7|24|25|129|129|0|100|3|0|0|8|0|4|0|0|7|
37
<span style="color:green">ACK from 47</span>
38
39 53 Alessio Valeri
## 50 - 35 interaction
40
41 57 Alessio Valeri
<span style="color:darkorange">|50|0|9|1|1|1|0|240|248|</span>
42 1 Alessio Valeri
<span style="color:green">ACK from 35</span>
43 59 Alessio Valeri
|35|0|36|1|0|1|1|255|0|40|32|0|0|0|2|0|3|34|128|31|0|31|128|18|170|0|0|0|41|41|1|3|241|208|0|106|
44 54 Alessio Valeri
<span style="color:green">ACK from 50</span>
45 57 Alessio Valeri
<span style="color: darkorange">|50|0|28|1|1|1|0|255|24|32|0|7|24|33|129|34|30|30|0|0|25|0|62|0|6|0|2|100|</span>
46 54 Alessio Valeri
<span style="color:green">ACK from 35</span>
47 59 Alessio Valeri
|35|0|14|1|0|1|1|254|16|32|16|32|0|241|
48 54 Alessio Valeri
<span style="color:green">ACK from 50</span>
49 57 Alessio Valeri
<span style="color: darkorange">|50|0|32|1|1|1|0|159|31|129|129|20|60|0|7|129|31|26|100|3|0|0|0|0|0|0|0|0|0|2|0|111|</span>
50 53 Alessio Valeri
<span style="color:green">ACK from 35</span>
51
52 1 Alessio Valeri
## 63 - 243 interaction
53 52 Alessio Valeri
54 61 Alessio Valeri
<span style="color:darkorange">|63|1|9|202|160|1|0|0|99|</span>
55 50 Alessio Valeri
<span style="color:green">ACK from 243</span>
56 45 Alessio Valeri
|243|1|48|1|0|0|255|192|6|0|0|2|0|0|0|0|0|0|0|0|0|66|34|18|178|0|0|60|20|31|0|9|31|0|145|0|0|0|0|33|0|24|0|30|0|0|0|92|
57 61 Alessio Valeri
<span style="color:darkorange">|63|1|9|202|160|1|0|1|98|</span>
58 50 Alessio Valeri
<span style="color:green">ACK from 243</span>
59 45 Alessio Valeri
|243|1|48|1|0|0|255|193|6|0|0|0|0|26|0|0|0|0|7|0|0|0|129|0|0|0|31|0|0|100|31|0|0|0|0|3|129|0|0|0|0|0|129|0|0|0|0|243|
60 1 Alessio Valeri
61 152 Alessio Valeri
## DEVICE DISCOVERY
62 154 Alessio Valeri
When the Hi-mit interface is looking for devices on H-LINK bus the following messages are sent: (This messages were logged with **no device connected**  on H-LINK bus)
63 152 Alessio Valeri
64 167 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR| | | |CRC |
65 152 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
66 153 Alessio Valeri
|41|0|9|202|160|255|255|241|146|
67 1 Alessio Valeri
68 167 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR  | | | |  |CRC |
69 153 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
70 155 Alessio Valeri
|57|3|10|202|160|255|255|0|0|99|
71 152 Alessio Valeri
72 65 Alessio Valeri
## AUTODISCOVERY ??
73 73 Alessio Valeri
From time to time these messages appears on the bus, they are not always grouped together and they are not acknowledged, maybe they are used to report their presence ?
74 65 Alessio Valeri
75 85 Alessio Valeri
76 90 Alessio Valeri
|35|0|10|1|0|1|255|15|20|238| <- UPDATE: VALUE 15 & 20 CHANGE OVER TIME, ARE THEY TEMPERATURE ?
77 65 Alessio Valeri
|50|0|9|1|1|1|255|241|6|
78 1 Alessio Valeri
|41|0|9|202|160|255|255|241|146|
79 86 Alessio Valeri
80
|35|0|28|1|0|1|255|242|3|34|128|31|0|31|128|18|170|0|0|0|41|41|1|3|241|208|0|171| -> This is a status update but it seems no one requests or acknowledge
81 45 Alessio Valeri
82 62 Alessio Valeri
## ALL MESSAGES
83 75 Alessio Valeri
Here are reported all the messages captured :
84 45 Alessio Valeri
85 177 Alessio Valeri
Note: DSW8 ADDR field is the binary encoded value +1
86
Example: 
87
![](clipboard-202508070058-zy4vb.png)
88
In the image above DSW8 ADDR is equal to 8+1 = **9**
89
90
DSW1 field is thebynary encoded value set on the Hi-mit interface
91
92
93 11 Alessio Valeri
### ADDRESS 41 ( HI-MIT INTERFACE )
94 163 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR | | | |CRC |
95 91 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
96 1 Alessio Valeri
|41|0|9|202|160|255|255|241|146|
97 92 Alessio Valeri
98 176 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR | DSW8 ADDR | | |CRC |
99 92 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
100 1 Alessio Valeri
|41|0|9|202|160|1|1|97|2|
101 2 Alessio Valeri
102 163 Alessio Valeri
| SRC | CTRL | LEN | | DSW1 ADDR | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | |  | |  | | | | | CRC | 
103 91 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
104 4 Alessio Valeri
|41|0|48|202|160|1|1|107|62|31|8|255|11|12|45|24|0|0|26|28|28|28|28|28|28|28|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|211|
105 92 Alessio Valeri
106 163 Alessio Valeri
| SRC | CTRL | LEN | | DSW1 ADDR | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | CRC | 
107 92 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
108 1 Alessio Valeri
|41|0|48|202|160|1|1|107|62|0|8|0|11|12|45|24|0|0|26|28|28|28|28|28|28|28|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|51|
109 5 Alessio Valeri
110 237 Alessio Valeri
## Address 146
111 108 Alessio Valeri
Messages coming from 146 seems to be associated with the master controller status.
112 1 Alessio Valeri
113 210 Alessio Valeri
**The following message is sent when there is a parameter change on MASTER CONTROLLER:**
114
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | PARAMETER ID | SET VALUE | CRC |
115
|--|--|--|--|--|--|--|--|--|--|--|--|
116 226 Alessio Valeri
|146|0|12|1|1|1|0| 99 |62| **x** | **x** | xx |
117 1 Alessio Valeri
118 226 Alessio Valeri
Multiple parameters can be concatenated in a request  in the following way: 
119
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | PARAMETER ID x1 | SET VALUE x1 |PARAMETER ID x2 | SET VALUE x2 |PARAMETER ID xn | SET VALUE xn | CRC |
120 227 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
121 228 Alessio Valeri
|146|0| 10+(n*2) |1|1|1|0| 99 |62| xx | xx |xx| xx |xx | xx | xx |
122 215 Alessio Valeri
123 229 Alessio Valeri
#### PARAMETERS ID
124
These are the parameters ID :
125 210 Alessio Valeri
| DESCRIPTION |PARAMETER ID |
126
|--|--|
127 216 Alessio Valeri
| **MODE**              | 1 |
128 243 Alessio Valeri
| CYCLE MODE?           | 2 |
129 216 Alessio Valeri
| **CYCLE1 WATER TEMP** | 3 |
130
| **CYCLE2 WATER TEMP** | 4 |
131
| **DHW SET TEMP**      | 5 |
132
| **POOL SET TEMP**     | 6 |
133 252 Alessio Valeri
| **ERROR CODE**     | 7 |
134 260 Alessio Valeri
| ?     | 8 |
135 221 Alessio Valeri
| ?     | 9 |
136 216 Alessio Valeri
| **ROOM1 SET TEMP**    | 10 |
137 215 Alessio Valeri
| UNKNOWN TEMP          | 11 |
138
| UNKNOWN TEMP          | 12 |
139
| UNKNOWN TEMP          | 13 |
140
| UNKNOWN TEMP          | 14 |
141
| UNKNOWN TEMP          | 15 |
142
| UNKNOWN TEMP          | 16 |
143 240 Alessio Valeri
| UNKNOWN TEMP          | 17 |
144
| **ROOM ENABLE**       | 18 |
145 241 Alessio Valeri
| **ROOM ECO MODE?**       | 19 |
146 245 Alessio Valeri
| DHW CONFIG ?           | 20 |
147 280 Alessio Valeri
| **PUMP STATUS**  | 21 |
148 223 Alessio Valeri
| WATER PUMP CONFIG?        | 22 |
149 215 Alessio Valeri
150
#### MODE
151 253 Alessio Valeri
152
| BIT 7 | BIT 6  | BIT 5 | BIT 4 | BIT 3 | BIT 2 |  BIT 1| BIT 0 |
153
|--|--|--|--|--|--|--|--|
154 257 Alessio Valeri
| | HEAT MODE |  |  | COOL MODE | AUTO MODE | CYCLE 2 ENABLE | CYCLE1 ENABLE |
155 253 Alessio Valeri
156 272 Alessio Valeri
This parameter sets the working mode of the unit: HEAT / COOL / AUTO. Only one of the 3 mode can be active at a time.
157 215 Alessio Valeri
When there is a change of the working mode on the master controller also the following parameters are updated in a single request.
158 1 Alessio Valeri
3,4,10,11,12,13,14,15,16,17
159
160 230 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | MODE: | VALUE | CYCLE1 SET TEMP: | VALUE | CYCLE2 SET TEMP: | VALUE | ROOM1 SET TEMP: | VALUE  | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | CRC |
161 225 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
162 224 Alessio Valeri
|146|0|32|9|1|9|0|99|62|1|8|3|6|4|12|10|23|11|28|12|28|13|28|14|28|15|28|16|28|17|28|115|
163
164 246 Alessio Valeri
#### CYCLE MODE: 16 (CYCLE1 ECO MODE OFF),17 (CYCLE1 ECO MODE ON)
165 248 Alessio Valeri
166 249 Alessio Valeri
| BIT 7 | BIT 6  | BIT 5 | BIT 4 | BIT 3 | BIT 2 |  BIT 1| BIT 0 |
167 248 Alessio Valeri
|--|--|--|--|--|--|--|--|
168 263 Alessio Valeri
|? | ? | ? |  PUMP ENABLE ? | ? | ? |CYCLE2 ECO MODE| CYCLE1 ECO MODE |
169 248 Alessio Valeri
170 246 Alessio Valeri
#### DHW CONFIG: 0 DHW BOOST OFF, 128 DHW BOOST ON
171 213 Alessio Valeri
172 279 Alessio Valeri
#### PUMP STATUS : IT IS 128 WHEN PUMP IS RUNNING, CHANGE TO 0 WHEN STOPS
173 269 Alessio Valeri
174 278 Alessio Valeri
#### WATERPUMP CONFIG? :  SEEN VALUES: 32,128,160,192,224
175
176
192 ->(HEAT MODE SELECTED)
177 1 Alessio Valeri
178 277 Alessio Valeri
|BIT 7 |BIT 6 |BIT 5 |BIT 4 |BIT 3 |BIT 2 |BIT 1 |BIT 0 |
179
|--|--|--|--|--|--|--|--|
180
| WP ECO MODE HEAT | WP ECO MODE COOL  | 1 | 0 | 0 | 0 | 0 | 0 |
181
182 212 Alessio Valeri
**EXAMPLE:** The following message is sent when the MASTER CONTROLLER POOL water set temp is changed to 27°C :
183 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | POOL WATER TEMP | SET TEMP | CRC |
184 135 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
185 139 Alessio Valeri
|146|0|12|1|1|1|0| 99 |62| **6** | **27** |77| 
186
187 13 Alessio Valeri
188 14 Alessio Valeri
**Inviato quando seleziono la modalità HEAT**
189 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | MODE ?  |  | |  | | |  | | | | | | | | | | |  | | CRC |
190 104 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
191 16 Alessio Valeri
|146|0|30|1|1|1|0|99|62|1| **64** |3|20|4|20|11|22|12|22|13|22|14|22|15|22|16|22|17|22|24|
192 104 Alessio Valeri
193 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | | CRC |
194 105 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
195 14 Alessio Valeri
|146|0|12|1|1|1|0|99|62|22|128|198|
196
197
**Inviato quando seleziono la modalità COLD**
198 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | MODE ?  |  | |  | | |  | | | | | | | | | | |  | | CRC |
199 104 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
200 16 Alessio Valeri
|146|0|30|1|1|1|0|99|62|1| **8** |3|13|4|16|11|28|12|28|13|28|14|28|15|28|16|28|17|28|71|
201 104 Alessio Valeri
202 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | | CRC |
203 105 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
204 14 Alessio Valeri
|146|0|12|1|1|1|0|99|62|22|160|230|
205
206
**Inviato quando seleziono la modalità AUTO**
207 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | |  MODE ? |  | |  | | |  | | | | | | | | | |  | CRC |
208 16 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
209 14 Alessio Valeri
|146|0|28|1|1|1|0|99|62|1| **4** |3|28|11|0|12|0|13|0|14|0|15|0|16|0|17|0|80|
210
211 231 Alessio Valeri
#### STATUS UPDATE MESSAGE
212 1 Alessio Valeri
213 270 Alessio Valeri
~~**The following 48Byte seems to be a periodic status update message**~~ 
214
This status update message is requested periodically by 41 with the following request:
215
|41|0|9|202|161|9|1|97|11|
216
217 247 Alessio Valeri
The parameter are in the same order as the table above: 1) MODE, 2)PUMP, 3) WATER SET TEMP, ETC ..
218 264 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | - | - | | MODE | PUMP?? | WATER SET TEMP CYCLE1 | WATER SET TEMP CYCLE2 | DHW SET TEMP | POOL SET TEMP | ERROR CODE | | | ROOM 1 SET TEMP | | | | | | | | ROOM ENABLE | | DHW CONFIG | UNK1 | WATERPUMP CONFIG | | | | | | |  | |  |  | | | | | | CRC | 
219 107 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
220 1 Alessio Valeri
|146|0|48|1|1|1|0|97|62|0|8|0| **11** |12|45|24|0|0|0|26|28|28|28|28|28|28|28|0|0|0|0|160|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|242|
221 208 Alessio Valeri
222
**MODE** : 4/5(AUTO), 8/9(COOL), 64/65(HEAT)
223
**ROOM ENABLE** : 1(ROOM 1),
224
**UNK1** : SEEN VALUES: 0,128
225
**WATERPUMP CONFIG** : SEEN VALUES: 32,128,160,192,224 ( SEE FOLLOWING TABLE )
226
227 209 Alessio Valeri
**ERROR CODE** : SEEN VALUES: A1,A5
228 19 Alessio Valeri
229 292 Alessio Valeri
### ADDRESS 50 ( INDOOR UNIT )
230 207 Alessio Valeri
| SRC | CTRL |LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | CRC |
231 95 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
232 1 Alessio Valeri
|50|0|9|1|1|1|0|240|248|
233 95 Alessio Valeri
234 207 Alessio Valeri
| SRC | CTRL |LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | CRC |
235 95 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
236 42 Alessio Valeri
|50|0|9|1|1|1|255|241|6|
237
238 101 Alessio Valeri
239 185 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR |- | DSW8 ADDR |- |- |- | MODE | PUMP ? | WATER SET TEMP | ? | IDU GAS TEMPERATURE |- | IDU LIQUID TEMPERATURE | ~~WATER OUT PHEX TEMP~~ NOT SURE | WATER INLET TEMP | | | | | | | | |  | CRC |
240 101 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
241 1 Alessio Valeri
|50|0|28|1|1|1|0|255|24|32| *0* |22|24| **16** |129|20| **11** |12|0|0|22|0|62|0|6|0|2|122|
242 128 Alessio Valeri
243 129 Alessio Valeri
MODE is 32 when CYCLE 1 is OFF, when COOL MODE on CYCLE1 is enabled it changes to 9.
244 130 Alessio Valeri
PUMP ? becomes 1 when cooling is enabled. Change to 17 when water pump is running. <- **EDIT: NOT 100% SURE** (PUMP SEEMS TO RUN EVEN WHEN PUMP=1 , MAYBE 1->CYCLE 1 ENABLED AND 17-> CYCLE1&ROOM1 ENABLED)
245 129 Alessio Valeri
WATER SET TEMP IS SET WHEN CYCLE 1 IS ENABLED
246 23 Alessio Valeri
247 289 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | WATER OUT TEMP ? | | | | | | | | AMBIENT TEMP (SIMILAR VALUE) |  | REQUESTED PUMP PWM | | FLOW ?| | | | | | | | | ? | | CRC | 
248 113 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
249 1 Alessio Valeri
|50|0|32|1|1|1|0|159|30|129|129|20|60|0|7|129|30|26|100|3|0|0|0|0|0|0|0|0|0|2|0|111|
250
251 289 Alessio Valeri
AMBIENT TEMP -> **COULD BE TEMP SENSOR INSIDE INDOOR UNIT REPORTING A SIMILAR VALUE TO OUTDOOR AMBIENT TEMP**
252 290 Alessio Valeri
REQUESTED PUMP PWM -> I THINK IT IS REQUESTED PWM BECAUSE WHEN VALUE IS 100 (PWM 100 MEANS OFF) SOMETIME THE PUMP IS STILL ON
253 284 Alessio Valeri
?->CYCLE1 HEAT ON : 4 CYCLE 1 HEAT OFF: 0, CYCLE 1 COOL ON: 6, CYCLE 1 COOL OFF: 2
254 43 Alessio Valeri
255 293 Alessio Valeri
### ADDRESS 35 ( OUTDOOR UNIT )
256 27 Alessio Valeri
257 172 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | CRC |
258 96 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
259
|35|0|10|1|0|1|255|15|20|238|
260 1 Alessio Valeri
261 172 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | | | |  | CRC |
262 96 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
263
|35|0|14|1|0|1|1|254|16|32|16|32|0|241|
264 1 Alessio Valeri
265 190 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | | | EVAP GAS TEMP | | DISCHARGER TEMPERATURE | | ~~IDU LIQUID TEMP~~ | | FREQUENCE | CURRENT | EVO% | | | | | | |  | CRC |
266 96 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
267 26 Alessio Valeri
|35|0|28|1|0|1|255|242|3|22|128| **25** |0| **51** |128| **17** |110|0|0|0|41|41|1|3|241|208|0|114|
268
269 114 Alessio Valeri
270
271 190 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | | | | | | | | | OUTDOOR TEMP | | EVAP GAS TEMP | | DISCHARGER TEMPERATURE |  | ~~IDU LIQUID TEMP~~ | | FREQUENCE | CURRENT | EVO% | | | | | | | | CRC | 
272 114 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
273
|35|0|36|1|0|1|1|255|0|40|32|0|0|0|2|0|3|20|128| **22** |0| **42** |128| **14**| 100|0|0|0|41|41|1|3|241|208|0|178|
274 115 Alessio Valeri
275 32 Alessio Valeri
Message similar to the previous one with added 8 byte.
276
277 168 Alessio Valeri
|35|240|8|9|224|9|255|231| -> SENT WHEN THERE IS NO COMMUNICATION WITH OUDOOR UNIT ? LOOKS LIKE A DISCOVERY MESSAGE
278
279 158 Alessio Valeri
### ADDRESS 47 ( HI-MIT INTERFACE )
280 78 Alessio Valeri
281 1 Alessio Valeri
Unit 47 seems to send only this request that 242 replies to
282 79 Alessio Valeri
283 171 Alessio Valeri
|SRC | CTRL | LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? | ? | CRC |
284 100 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
285 1 Alessio Valeri
|47|0|10|202|160|1|1|108|0|12|
286 160 Alessio Valeri
287
### ADDRESS 57 ( HI-MIT INTERFACE )
288
289
This message is seen during device discovery
290
291 165 Alessio Valeri
|SRC | CTRL | LEN | - | DSW1 ADDR | ? | ? | ? | ? | CRC |
292 1 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
293 161 Alessio Valeri
|57|3|10|202|160|255|255|0|0|99|
294 36 Alessio Valeri
295 159 Alessio Valeri
### ADDRESS 63 ( HI-MIT INTERFACE )
296 81 Alessio Valeri
Unit 63 seems to only send request that 243 replies to. No other messages are captured at this time.
297
298 169 Alessio Valeri
|SRC | CTRL |LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? |CRC |
299 98 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
300
|63|1|9|202|160|1|0|0|99|
301
302 169 Alessio Valeri
|SRC | CTRL |LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? |CRC |
303 98 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
304
|63|1|9|202|160|1|0|1|98|
305 41 Alessio Valeri
306 199 Alessio Valeri
### ADDRESS 242 (UNKNOWN)
307
308 204 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | |WATER TEMP | | | ROOM1 TEMP ? |  | | | | | | | ROOM1 SET TEMP | | | | | | | | | | | | | | | | | WATER PUMP SPEED | | WATER FLOW (1 digit) |  | | | | | | CRC | 
309 199 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
310
|242|0|48|1|1|1|1|108|62|0| **7** |129|129|27|0|0|0|0|0|0|0|22|0|0|0|0|0|0|0|20|60|50|20|24|12|129|129|0| **14** |3| **14** |0|24|2|4|1|1|111|
311
312 41 Alessio Valeri
### ADDRESS 243 (UNKNOWN)
313 1 Alessio Valeri
Unit 243 seems to reply to 63 requests.
314 187 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR  | | | | | | | | | | | | | | | FREQUENCY | | TARGET FREQUENCY | | OUTDOOR TEMP | | | | | | | DISCHARGER TEMP | | | | | | | | |  | | FREQUENCE | | | EVAP GAS TEMP | | | | CRC | 
315 99 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
316
|243|1|48|1|0|0|255|192|6|0|0|2|0|0|0|0|0|0|0|0|0|64|30|17|159|0|0|60|20|30|0|1|30|0|145|0|0|0|0|34|0|24|0|29|0|0|0|68|
317 1 Alessio Valeri
318 206 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | | | | | | | | | | | FREQUENCE |  | | | | | | | | | | | |  | WATER PUMP SPEED? | | | | | | | | |  | |  | WATER FLOW? | | | | | | CRC | 
319 99 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
320
|243|1|48|1|0|0|255|193|6|0|0|0|0|26|0|0|0|0|7|0|0|0|129|0|0|0|29|0|0|100|29|0|0|0|0|3|129|0|0|0|0|0|129|0|0|0|0|243|
Redmine Appliance - Powered by TurnKey Linux