Observing the traffic on the bus we can see there are different units. These are the address found on the 12 bus :
| ADDRESS | UNIT |
|---|---|
| 41 | Hi-Mit remote controller |
| 47 | Hi-Mit remote controller |
| 50 | Indoor Unit |
| 57 | Hi-Mit remote controller |
| 63 | Hi-Mit remote controller |
| 34 | |
| 35 | Outodoor Unit |
| 146 | Indoor Unit |
| 242 | |
| 243 |
REQUESTS / REPLIES ANALYSIS¶
Here I try to report any communication pattern I can find :
41 - 146 interaction¶
Messages exchanged between Hi-mit interface and outdoor unit
WIP
47 - 242 interaction¶
|47|0|10|202|160|1|1|108|0|12|
ACK from 242
|242|0|48|1|1|1|1|108|62|0|31|129|129|27|0|0|0|0|0|0|0|22|0|0|0|0|0|0|0|20|60|50|7|24|25|129|129|0|100|3|0|0|8|0|4|0|0|7|
ACK from 47
50 - 35 interaction¶
|50|0|9|1|1|1|0|240|248|
ACK from 35
|35|0|36|1|0|1|1|255|0|40|32|0|0|0|2|0|3|34|128|31|0|31|128|18|170|0|0|0|41|41|1|3|241|208|0|106|
ACK from 50
|50|0|28|1|1|1|0|255|24|32|0|7|24|33|129|34|30|30|0|0|25|0|62|0|6|0|2|100|
ACK from 35
|35|0|14|1|0|1|1|254|16|32|16|32|0|241|
ACK from 50
|50|0|32|1|1|1|0|159|31|129|129|20|60|0|7|129|31|26|100|3|0|0|0|0|0|0|0|0|0|2|0|111|
ACK from 35
63 - 243 interaction¶
|63|1|9|202|160|1|0|0|99|
ACK from 243
|243|1|48|1|0|0|255|192|6|0|0|2|0|0|0|0|0|0|0|0|0|66|34|18|178|0|0|60|20|31|0|9|31|0|145|0|0|0|0|33|0|24|0|30|0|0|0|92|
|63|1|9|202|160|1|0|1|98|
ACK from 243
|243|1|48|1|0|0|255|193|6|0|0|0|0|26|0|0|0|0|7|0|0|0|129|0|0|0|31|0|0|100|31|0|0|0|0|3|129|0|0|0|0|0|129|0|0|0|0|243|
DEVICE DISCOVERY¶
When the Hi-mit interface is looking for devices on H-LINK bus the following messages are sent: (This messages were logged with no device connected on H-LINK bus)
| SRC | CTRL | LEN | DSW1 ADDR | CRC | ||||
|---|---|---|---|---|---|---|---|---|
| 41 | 0 | 9 | 202 | 160 | 255 | 255 | 241 | 146 |
| SRC | CTRL | LEN | DSW1 ADDR | CRC | |||||
|---|---|---|---|---|---|---|---|---|---|
| 57 | 3 | 10 | 202 | 160 | 255 | 255 | 0 | 0 | 99 |
AUTODISCOVERY ??¶
From time to time these messages appears on the bus, they are not always grouped together and they are not acknowledged, maybe they are used to report their presence ?
|35|0|10|1|0|1|255|15|20|238| <- UPDATE: VALUE 15 & 20 CHANGE OVER TIME, ARE THEY TEMPERATURE ?
|50|0|9|1|1|1|255|241|6|
|41|0|9|202|160|255|255|241|146|
|35|0|28|1|0|1|255|242|3|34|128|31|0|31|128|18|170|0|0|0|41|41|1|3|241|208|0|171| -> This is a status update but it seems no one requests or acknowledge
ALL MESSAGES¶
Here are reported all the messages captured :
Note: DSW8 ADDR field is the binary encoded value +1
Example:

In the image above DSW8 ADDR is equal to 8+1 = 9
DSW1 field is thebynary encoded value set on the Hi-mit interface
ADDRESS 41 ( HI-MIT INTERFACE )¶
| SRC | CTRL | LEN | DSW1 ADDR | CRC | ||||
|---|---|---|---|---|---|---|---|---|
| 41 | 0 | 9 | 202 | 160 | 255 | 255 | 241 | 146 |
| SRC | CTRL | LEN | DSW1 ADDR | DSW8 ADDR | CRC | |||
|---|---|---|---|---|---|---|---|---|
| 41 | 0 | 9 | 202 | 160 | 1 | 1 | 97 | 2 |
| SRC | CTRL | LEN | DSW1 ADDR | CRC | |||||||||||||||||||||||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 41 | 0 | 48 | 202 | 160 | 1 | 1 | 107 | 62 | 31 | 8 | 255 | 11 | 12 | 45 | 24 | 0 | 0 | 26 | 28 | 28 | 28 | 28 | 28 | 28 | 28 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 211 |
| SRC | CTRL | LEN | DSW1 ADDR | CRC | |||||||||||||||||||||||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 41 | 0 | 48 | 202 | 160 | 1 | 1 | 107 | 62 | 0 | 8 | 0 | 11 | 12 | 45 | 24 | 0 | 0 | 26 | 28 | 28 | 28 | 28 | 28 | 28 | 28 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 51 |
ADDRESS 146 ( INDOOR UNIT )¶
Messages coming from 146 seems to be associated with the master controller status.
The following message is sent when there is a parameter change on MASTER CONTROLLER:
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | PARAMETER ID | SET VALUE | CRC |
|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 12 | 1 | 1 | 1 | 0 | 99 | 62 | x | x | xx |
Multiple parameters can be concatenated in a request in the following way:
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | PARAMETER ID x1 | SET VALUE x1 | PARAMETER ID x2 | SET VALUE x2 | PARAMETER ID xn | SET VALUE xn | CRC |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 10+(n*2) | 1 | 1 | 1 | 0 | 99 | 62 | xx | xx | xx | xx | xx | xx | xx |
PARAMETERS ID¶
These are the parameters ID :
| DESCRIPTION | PARAMETER ID |
|---|---|
| MODE | 1 |
| UNKNOWN | 2 |
| CYCLE1 WATER TEMP | 3 |
| CYCLE2 WATER TEMP | 4 |
| DHW SET TEMP | 5 |
| POOL SET TEMP | 6 |
| DHW/POOL MODE | 7 |
| ? | 9 |
| ROOM1 SET TEMP | 10 |
| UNKNOWN TEMP | 11 |
| UNKNOWN TEMP | 12 |
| UNKNOWN TEMP | 13 |
| UNKNOWN TEMP | 14 |
| UNKNOWN TEMP | 15 |
| UNKNOWN TEMP | 16 |
| UNKNOWN TEMP | 17 |
| UNKNOWN | 21 |
| WATER PUMP CONFIG? | 22 |
MODE¶
This parameter sets the working mode of the unit: HEAT / COOL / AUTO
When there is a change of the working mode on the master controller also the following parameters are updated in a single request.
3,4,10,11,12,13,14,15,16,17
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | MODE: | VALUE | CYCLE1 SET TEMP: | VALUE | CYCLE2 SET TEMP: | VALUE | ROOM1 SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | CRC |
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 32 | 9 | 1 | 9 | 0 | 99 | 62 | 1 | 8 | 3 | 6 | 4 | 12 | 10 | 23 | 11 | 28 | 12 | 28 | 13 | 28 | 14 | 28 | 15 | 28 | 16 |
DHW/POOL MODE**: 0 -> OFF, 162 -> POOL ENABLED, 22 -> DHW ENABLED¶
EXAMPLE: The following message is sent when the MASTER CONTROLLER POOL water set temp is changed to 27°C :
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | POOL WATER TEMP | SET TEMP | CRC | |||
|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 12 | 1 | 1 | 1 | 0 | 99 | 62 | 6 | 27 | 77 |
The following message is sent when the MASTER CONTROLLER POOL OR DHW is changed to DISABLED :
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | POOL/DHW | SET VALUE | CRC | |||
|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 12 | 1 | 1 | 1 | 0 | 99 | 62 | 7 | 0 | 87 |
ALSO THE FOLLOWING MESSAGE:
|146|0|43|1|1|1|0|96|62|0|0|73|119|185|131|9|0|0|16|2|64|1|0|24|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|50|
The following message is sent when the MASTER CONTROLLER POOL is changed to ENABLED :
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | POOL/DHW | SET VALUE | CRC | |||
|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 12 | 1 | 1 | 1 | 0 | 99 | 62 | 7 | 162 | 145 |
ALSO THE FOLLOWING MESSAGE:
|146|0|43|1|1|1|0|96|62|0|0|73|119|185|131|9|0|0|16|130|64|1|0|24|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|178|
The following message is sent when the MASTER CONTROLLER DHW is changed to ENABLED :
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | POOL/DHW | SET VALUE | CRC | |||
|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 12 | 1 | 1 | 1 | 0 | 99 | 62 | 7 | 22 | 65 |
ALSO THE FOLLOWING MESSAGE:
|146|0|43|1|1|1|0|96|62|0|0|73|119|185|131|9|0|0|16|34|64|1|0|24|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|18|
Inviato quando seleziono la modalità HEAT
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | MODE ? | CRC | ||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 30 | 1 | 1 | 1 | 0 | 99 | 62 | 1 | 64 | 3 | 20 | 4 | 20 | 11 | 22 | 12 | 22 | 13 | 22 | 14 | 22 | 15 | 22 | 16 | 22 | 17 | 22 | 24 |
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | CRC | |||||
|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 12 | 1 | 1 | 1 | 0 | 99 | 62 | 22 | 128 | 198 |
Inviato quando seleziono la modalità COLD
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | MODE ? | CRC | ||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 30 | 1 | 1 | 1 | 0 | 99 | 62 | 1 | 8 | 3 | 13 | 4 | 16 | 11 | 28 | 12 | 28 | 13 | 28 | 14 | 28 | 15 | 28 | 16 | 28 | 17 | 28 | 71 |
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | CRC | |||||
|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 12 | 1 | 1 | 1 | 0 | 99 | 62 | 22 | 160 | 230 |
Inviato quando seleziono la modalità AUTO
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | MODE ? | CRC | ||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 28 | 1 | 1 | 1 | 0 | 99 | 62 | 1 | 4 | 3 | 28 | 11 | 0 | 12 | 0 | 13 | 0 | 14 | 0 | 15 | 0 | 16 | 0 | 17 | 0 | 80 |
STATUS UPDATE MESSAGE¶
The following 48Byte seems to be a periodic status update message
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | MODE | PUMP?? | WATER SET TEMP CYCLE1 | WATER SET TEMP CYCLE2 | DHW SET TEMP | POOL SET TEMP | ERROR CODE ? | ROOM 1 SET TEMP | ROOM ENABLE | UNK1 | UNK2 | CRC | ||||||||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 146 | 0 | 48 | 1 | 1 | 1 | 0 | 97 | 62 | 0 | 8 | 0 | 11 | 12 | 45 | 24 | 0 | 0 | 0 | 26 | 28 | 28 | 28 | 28 | 28 | 28 | 28 | 0 | 0 | 0 | 0 | 160 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 242 |
MODE : 4/5(AUTO), 8/9(COOL), 64/65(HEAT)
PUMP : 16 ENABLED ?
ROOM ENABLE : 1(ROOM 1),
UNK1 : SEEN VALUES: 0,128
UNK2 : SEEN VALUES: 32,160,224 ( SEE FOLLOWING TABLE )
| 7 | 6 | 5 | 4 | 3 | 2 | 1 | 0 |
|---|---|---|---|---|---|---|---|
| WP ECO MODE HEAT | WP ECO MODE COOL | 1 | 0 | 0 | 0 | 0 | 0 |
ERROR CODE : SEEN VALUES: A1,A5
ADDRESS 50 ( HI-MIT INTERFACE IDU )¶
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | CRC |
|---|---|---|---|---|---|---|---|---|
| 50 | 0 | 9 | 1 | 1 | 1 | 0 | 240 | 248 |
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | CRC |
|---|---|---|---|---|---|---|---|---|
| 50 | 0 | 9 | 1 | 1 | 1 | 255 | 241 | 6 |
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | MODE | PUMP ? | WATER SET TEMP | ? | IDU GAS TEMPERATURE | - | IDU LIQUID TEMPERATURE |
|
WATER INLET TEMP | CRC | |||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 50 | 0 | 28 | 1 | 1 | 1 | 0 | 255 | 24 | 32 | 0 | 22 | 24 | 16 | 129 | 20 | 11 | 12 | 0 | 0 | 22 | 0 | 62 | 0 | 6 | 0 | 2 | 122 |
MODE is 32 when CYCLE 1 is OFF, when COOL MODE on CYCLE1 is enabled it changes to 9.
PUMP ? becomes 1 when cooling is enabled. Change to 17 when water pump is running. <- EDIT: NOT 100% SURE (PUMP SEEMS TO RUN EVEN WHEN PUMP=1 , MAYBE 1->CYCLE 1 ENABLED AND 17-> CYCLE1&ROOM1 ENABLED)
WATER SET TEMP IS SET WHEN CYCLE 1 IS ENABLED
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | TEMP? | CRC | ||||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 50 | 0 | 32 | 1 | 1 | 1 | 0 | 159 | 30 | 129 | 129 | 20 | 60 | 0 | 7 | 129 | 30 | 26 | 100 | 3 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 2 | 0 | 111 |
ADDRESS 35 (UNKNOWN)¶
| SRC | CTRL | LEN | DSW8 ADDR | DSW8 ADDR | CRC | ||||
|---|---|---|---|---|---|---|---|---|---|
| 35 | 0 | 10 | 1 | 0 | 1 | 255 | 15 | 20 | 238 |
| SRC | CTRL | LEN | DSW8 ADDR | DSW8 ADDR | CRC | ||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 35 | 0 | 14 | 1 | 0 | 1 | 1 | 254 | 16 | 32 | 16 | 32 | 0 | 241 |
| SRC | CTRL | LEN | DSW8 ADDR | DSW8 ADDR | EVAP GAS TEMP | DISCHARGER TEMPERATURE | FREQUENCE | CURRENT | EVO% | CRC | |||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 35 | 0 | 28 | 1 | 0 | 1 | 255 | 242 | 3 | 22 | 128 | 25 | 0 | 51 | 128 | 17 | 110 | 0 | 0 | 0 | 41 | 41 | 1 | 3 | 241 | 208 | 0 | 114 |
| SRC | CTRL | LEN | DSW8 ADDR | DSW8 ADDR | OUTDOOR TEMP | EVAP GAS TEMP | DISCHARGER TEMPERATURE | FREQUENCE | CURRENT | EVO% | CRC | ||||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 35 | 0 | 36 | 1 | 0 | 1 | 1 | 255 | 0 | 40 | 32 | 0 | 0 | 0 | 2 | 0 | 3 | 20 | 128 | 22 | 0 | 42 | 128 | 14 | 100 | 0 | 0 | 0 | 41 | 41 | 1 | 3 | 241 | 208 | 0 | 178 |
Message similar to the previous one with added 8 byte.
|35|240|8|9|224|9|255|231| -> SENT WHEN THERE IS NO COMMUNICATION WITH OUDOOR UNIT ? LOOKS LIKE A DISCOVERY MESSAGE
ADDRESS 47 ( HI-MIT INTERFACE )¶
Unit 47 seems to send only this request that 242 replies to
| SRC | CTRL | LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? | ? | CRC |
|---|---|---|---|---|---|---|---|---|---|
| 47 | 0 | 10 | 202 | 160 | 1 | 1 | 108 | 0 | 12 |
ADDRESS 57 ( HI-MIT INTERFACE )¶
This message is seen during device discovery
| SRC | CTRL | LEN | - | DSW1 ADDR | ? | ? | ? | ? | CRC |
|---|---|---|---|---|---|---|---|---|---|
| 57 | 3 | 10 | 202 | 160 | 255 | 255 | 0 | 0 | 99 |
ADDRESS 63 ( HI-MIT INTERFACE )¶
Unit 63 seems to only send request that 243 replies to. No other messages are captured at this time.
| SRC | CTRL | LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? | CRC |
|---|---|---|---|---|---|---|---|---|
| 63 | 1 | 9 | 202 | 160 | 1 | 0 | 0 | 99 |
| SRC | CTRL | LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? | CRC |
|---|---|---|---|---|---|---|---|---|
| 63 | 1 | 9 | 202 | 160 | 1 | 0 | 1 | 98 |
ADDRESS 242 (UNKNOWN)¶
| SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | WATER TEMP | ROOM1 TEMP ? | ROOM1 SET TEMP | WATER PUMP SPEED | WATER FLOW (1 digit) | CRC | ||||||||||||||||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 242 | 0 | 48 | 1 | 1 | 1 | 1 | 108 | 62 | 0 | 7 | 129 | 129 | 27 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 22 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 20 | 60 | 50 | 20 | 24 | 12 | 129 | 129 | 0 | 14 | 3 | 14 | 0 | 24 | 2 | 4 | 1 | 1 | 111 |
ADDRESS 243 (UNKNOWN)¶
Unit 243 seems to reply to 63 requests.
| SRC | CTRL | LEN | DSW8 ADDR | FREQUENCY | TARGET FREQUENCY | OUTDOOR TEMP | DISCHARGER TEMP | FREQUENCE | EVAP GAS TEMP | CRC | |||||||||||||||||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 243 | 1 | 48 | 1 | 0 | 0 | 255 | 192 | 6 | 0 | 0 | 2 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 0 | 64 | 30 | 17 | 159 | 0 | 0 | 60 | 20 | 30 | 0 | 1 | 30 | 0 | 145 | 0 | 0 | 0 | 0 | 34 | 0 | 24 | 0 | 29 | 0 | 0 | 0 | 68 |
| SRC | CTRL | LEN | DSW8 ADDR | FREQUENCE | WATER PUMP SPEED? | WATER FLOW? | CRC | ||||||||||||||||||||||||||||||||||||||||
|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|---|
| 243 | 1 | 48 | 1 | 0 | 0 | 255 | 193 | 6 | 0 | 0 | 0 | 0 | 26 | 0 | 0 | 0 | 0 | 7 | 0 | 0 | 0 | 129 | 0 | 0 | 0 | 29 | 0 | 0 | 100 | 29 | 0 | 0 | 0 | 0 | 3 | 129 | 0 | 0 | 0 | 0 | 0 | 129 | 0 | 0 | 0 | 0 | 243 |
Updated by Alessio Valeri 5 months ago · 231 revisions