Project

General

Profile

Messages » History » Version 262

Alessio Valeri, 08/14/2025 03:30 AM

1 1 Alessio Valeri
# Messages
2 70 Alessio Valeri
3
Observing the traffic on the bus we can see there are different units. These are the address found on the 12 bus : 
4 21 Alessio Valeri
5 71 Alessio Valeri
|ADDRESS|UNIT |
6
|--|--|
7 72 Alessio Valeri
| 41 | Hi-Mit remote controller  |
8 1 Alessio Valeri
| 47 | Hi-Mit remote controller |
9 220 Alessio Valeri
| 50 | Indoor Unit |
10 151 Alessio Valeri
| 57 | Hi-Mit remote controller |
11 1 Alessio Valeri
| 63 | Hi-Mit remote controller |
12 150 Alessio Valeri
| 34 |  |
13 220 Alessio Valeri
| 35 | Outodoor Unit |
14 219 Alessio Valeri
| 146 | Indoor Unit |
15 150 Alessio Valeri
| 242 |  |
16
| 243 |  |
17
18 51 Alessio Valeri
# REQUESTS / REPLIES ANALYSIS
19 52 Alessio Valeri
 Here I try to report any communication pattern I can find :
20 1 Alessio Valeri
21 67 Alessio Valeri
## 41 - 146 interaction
22
Messages exchanged between Hi-mit interface and outdoor unit
23
WIP
24
25 52 Alessio Valeri
## 47 - 242 interaction
26 60 Alessio Valeri
<span style="color:darkorange">|47|0|10|202|160|1|1|108|0|12|</span>
27 52 Alessio Valeri
<span style="color:green">ACK from 242</span>
28
|242|0|48|1|1|1|1|108|62|0|31|129|129|27|0|0|0|0|0|0|0|22|0|0|0|0|0|0|0|20|60|50|7|24|25|129|129|0|100|3|0|0|8|0|4|0|0|7|
29
<span style="color:green">ACK from 47</span>
30
31 53 Alessio Valeri
## 50 - 35 interaction
32
33 57 Alessio Valeri
<span style="color:darkorange">|50|0|9|1|1|1|0|240|248|</span>
34 1 Alessio Valeri
<span style="color:green">ACK from 35</span>
35 59 Alessio Valeri
|35|0|36|1|0|1|1|255|0|40|32|0|0|0|2|0|3|34|128|31|0|31|128|18|170|0|0|0|41|41|1|3|241|208|0|106|
36 54 Alessio Valeri
<span style="color:green">ACK from 50</span>
37 57 Alessio Valeri
<span style="color: darkorange">|50|0|28|1|1|1|0|255|24|32|0|7|24|33|129|34|30|30|0|0|25|0|62|0|6|0|2|100|</span>
38 54 Alessio Valeri
<span style="color:green">ACK from 35</span>
39 59 Alessio Valeri
|35|0|14|1|0|1|1|254|16|32|16|32|0|241|
40 54 Alessio Valeri
<span style="color:green">ACK from 50</span>
41 57 Alessio Valeri
<span style="color: darkorange">|50|0|32|1|1|1|0|159|31|129|129|20|60|0|7|129|31|26|100|3|0|0|0|0|0|0|0|0|0|2|0|111|</span>
42 53 Alessio Valeri
<span style="color:green">ACK from 35</span>
43
44 1 Alessio Valeri
## 63 - 243 interaction
45 52 Alessio Valeri
46 61 Alessio Valeri
<span style="color:darkorange">|63|1|9|202|160|1|0|0|99|</span>
47 50 Alessio Valeri
<span style="color:green">ACK from 243</span>
48 45 Alessio Valeri
|243|1|48|1|0|0|255|192|6|0|0|2|0|0|0|0|0|0|0|0|0|66|34|18|178|0|0|60|20|31|0|9|31|0|145|0|0|0|0|33|0|24|0|30|0|0|0|92|
49 61 Alessio Valeri
<span style="color:darkorange">|63|1|9|202|160|1|0|1|98|</span>
50 50 Alessio Valeri
<span style="color:green">ACK from 243</span>
51 45 Alessio Valeri
|243|1|48|1|0|0|255|193|6|0|0|0|0|26|0|0|0|0|7|0|0|0|129|0|0|0|31|0|0|100|31|0|0|0|0|3|129|0|0|0|0|0|129|0|0|0|0|243|
52 1 Alessio Valeri
53 152 Alessio Valeri
## DEVICE DISCOVERY
54 154 Alessio Valeri
When the Hi-mit interface is looking for devices on H-LINK bus the following messages are sent: (This messages were logged with **no device connected**  on H-LINK bus)
55 152 Alessio Valeri
56 167 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR| | | |CRC |
57 152 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
58 153 Alessio Valeri
|41|0|9|202|160|255|255|241|146|
59 1 Alessio Valeri
60 167 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR  | | | |  |CRC |
61 153 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
62 155 Alessio Valeri
|57|3|10|202|160|255|255|0|0|99|
63 152 Alessio Valeri
64 65 Alessio Valeri
## AUTODISCOVERY ??
65 73 Alessio Valeri
From time to time these messages appears on the bus, they are not always grouped together and they are not acknowledged, maybe they are used to report their presence ?
66 65 Alessio Valeri
67 85 Alessio Valeri
68 90 Alessio Valeri
|35|0|10|1|0|1|255|15|20|238| <- UPDATE: VALUE 15 & 20 CHANGE OVER TIME, ARE THEY TEMPERATURE ?
69 65 Alessio Valeri
|50|0|9|1|1|1|255|241|6|
70 1 Alessio Valeri
|41|0|9|202|160|255|255|241|146|
71 86 Alessio Valeri
72
|35|0|28|1|0|1|255|242|3|34|128|31|0|31|128|18|170|0|0|0|41|41|1|3|241|208|0|171| -> This is a status update but it seems no one requests or acknowledge
73 45 Alessio Valeri
74 62 Alessio Valeri
## ALL MESSAGES
75 75 Alessio Valeri
Here are reported all the messages captured :
76 45 Alessio Valeri
77 177 Alessio Valeri
Note: DSW8 ADDR field is the binary encoded value +1
78
Example: 
79
![](clipboard-202508070058-zy4vb.png)
80
In the image above DSW8 ADDR is equal to 8+1 = **9**
81
82
DSW1 field is thebynary encoded value set on the Hi-mit interface
83
84
85 11 Alessio Valeri
### ADDRESS 41 ( HI-MIT INTERFACE )
86 163 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR | | | |CRC |
87 91 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
88 1 Alessio Valeri
|41|0|9|202|160|255|255|241|146|
89 92 Alessio Valeri
90 176 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR | DSW8 ADDR | | |CRC |
91 92 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
92 1 Alessio Valeri
|41|0|9|202|160|1|1|97|2|
93 2 Alessio Valeri
94 163 Alessio Valeri
| SRC | CTRL | LEN | | DSW1 ADDR | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | |  | |  | | | | | CRC | 
95 91 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
96 4 Alessio Valeri
|41|0|48|202|160|1|1|107|62|31|8|255|11|12|45|24|0|0|26|28|28|28|28|28|28|28|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|211|
97 92 Alessio Valeri
98 163 Alessio Valeri
| SRC | CTRL | LEN | | DSW1 ADDR | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | CRC | 
99 92 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
100 1 Alessio Valeri
|41|0|48|202|160|1|1|107|62|0|8|0|11|12|45|24|0|0|26|28|28|28|28|28|28|28|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|51|
101 5 Alessio Valeri
102 237 Alessio Valeri
## Address 146
103 108 Alessio Valeri
Messages coming from 146 seems to be associated with the master controller status.
104 1 Alessio Valeri
105 210 Alessio Valeri
**The following message is sent when there is a parameter change on MASTER CONTROLLER:**
106
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | PARAMETER ID | SET VALUE | CRC |
107
|--|--|--|--|--|--|--|--|--|--|--|--|
108 226 Alessio Valeri
|146|0|12|1|1|1|0| 99 |62| **x** | **x** | xx |
109 1 Alessio Valeri
110 226 Alessio Valeri
Multiple parameters can be concatenated in a request  in the following way: 
111
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | PARAMETER ID x1 | SET VALUE x1 |PARAMETER ID x2 | SET VALUE x2 |PARAMETER ID xn | SET VALUE xn | CRC |
112 227 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
113 228 Alessio Valeri
|146|0| 10+(n*2) |1|1|1|0| 99 |62| xx | xx |xx| xx |xx | xx | xx |
114 215 Alessio Valeri
115 229 Alessio Valeri
#### PARAMETERS ID
116
These are the parameters ID :
117 210 Alessio Valeri
| DESCRIPTION |PARAMETER ID |
118
|--|--|
119 216 Alessio Valeri
| **MODE**              | 1 |
120 243 Alessio Valeri
| CYCLE MODE?           | 2 |
121 216 Alessio Valeri
| **CYCLE1 WATER TEMP** | 3 |
122
| **CYCLE2 WATER TEMP** | 4 |
123
| **DHW SET TEMP**      | 5 |
124
| **POOL SET TEMP**     | 6 |
125 252 Alessio Valeri
| **ERROR CODE**     | 7 |
126 260 Alessio Valeri
| ?     | 8 |
127 221 Alessio Valeri
| ?     | 9 |
128 216 Alessio Valeri
| **ROOM1 SET TEMP**    | 10 |
129 215 Alessio Valeri
| UNKNOWN TEMP          | 11 |
130
| UNKNOWN TEMP          | 12 |
131
| UNKNOWN TEMP          | 13 |
132
| UNKNOWN TEMP          | 14 |
133
| UNKNOWN TEMP          | 15 |
134
| UNKNOWN TEMP          | 16 |
135 240 Alessio Valeri
| UNKNOWN TEMP          | 17 |
136
| **ROOM ENABLE**       | 18 |
137 241 Alessio Valeri
| **ROOM ECO MODE?**       | 19 |
138 245 Alessio Valeri
| DHW CONFIG ?           | 20 |
139 217 Alessio Valeri
| UNKNOWN            | 21 |
140 223 Alessio Valeri
| WATER PUMP CONFIG?        | 22 |
141 215 Alessio Valeri
142
#### MODE
143 253 Alessio Valeri
144
| BIT 7 | BIT 6  | BIT 5 | BIT 4 | BIT 3 | BIT 2 |  BIT 1| BIT 0 |
145
|--|--|--|--|--|--|--|--|
146 257 Alessio Valeri
| | HEAT MODE |  |  | COOL MODE | AUTO MODE | CYCLE 2 ENABLE | CYCLE1 ENABLE |
147 253 Alessio Valeri
148 257 Alessio Valeri
This parameter sets the working mode of the unit: HEAT / COOL / AUTO. Only one of the 3 mode can be active at a single time.
149 215 Alessio Valeri
When there is a change of the working mode on the master controller also the following parameters are updated in a single request.
150 1 Alessio Valeri
3,4,10,11,12,13,14,15,16,17
151
152 230 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | MODE: | VALUE | CYCLE1 SET TEMP: | VALUE | CYCLE2 SET TEMP: | VALUE | ROOM1 SET TEMP: | VALUE  | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | CRC |
153 225 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
154 224 Alessio Valeri
|146|0|32|9|1|9|0|99|62|1|8|3|6|4|12|10|23|11|28|12|28|13|28|14|28|15|28|16|28|17|28|115|
155
156 246 Alessio Valeri
#### CYCLE MODE: 16 (CYCLE1 ECO MODE OFF),17 (CYCLE1 ECO MODE ON)
157 248 Alessio Valeri
158 249 Alessio Valeri
| BIT 7 | BIT 6  | BIT 5 | BIT 4 | BIT 3 | BIT 2 |  BIT 1| BIT 0 |
159 248 Alessio Valeri
|--|--|--|--|--|--|--|--|
160 261 Alessio Valeri
|? | ? | ? |  PUMP ENABLE | ? | ? |CYCLE2 ECO MODE| CYCLE1 ECO MODE |
161 248 Alessio Valeri
162 246 Alessio Valeri
#### DHW CONFIG: 0 DHW BOOST OFF, 128 DHW BOOST ON
163 213 Alessio Valeri
164 212 Alessio Valeri
**EXAMPLE:** The following message is sent when the MASTER CONTROLLER POOL water set temp is changed to 27°C :
165 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | POOL WATER TEMP | SET TEMP | CRC |
166 135 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
167 139 Alessio Valeri
|146|0|12|1|1|1|0| 99 |62| **6** | **27** |77| 
168
169
170 13 Alessio Valeri
171 14 Alessio Valeri
**Inviato quando seleziono la modalità HEAT**
172 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | MODE ?  |  | |  | | |  | | | | | | | | | | |  | | CRC |
173 104 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
174 16 Alessio Valeri
|146|0|30|1|1|1|0|99|62|1| **64** |3|20|4|20|11|22|12|22|13|22|14|22|15|22|16|22|17|22|24|
175 104 Alessio Valeri
176 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | | CRC |
177 105 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
178 14 Alessio Valeri
|146|0|12|1|1|1|0|99|62|22|128|198|
179
180
**Inviato quando seleziono la modalità COLD**
181 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | MODE ?  |  | |  | | |  | | | | | | | | | | |  | | CRC |
182 104 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
183 16 Alessio Valeri
|146|0|30|1|1|1|0|99|62|1| **8** |3|13|4|16|11|28|12|28|13|28|14|28|15|28|16|28|17|28|71|
184 104 Alessio Valeri
185 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | | CRC |
186 105 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
187 14 Alessio Valeri
|146|0|12|1|1|1|0|99|62|22|160|230|
188
189
**Inviato quando seleziono la modalità AUTO**
190 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | |  MODE ? |  | |  | | |  | | | | | | | | | |  | CRC |
191 16 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
192 14 Alessio Valeri
|146|0|28|1|1|1|0|99|62|1| **4** |3|28|11|0|12|0|13|0|14|0|15|0|16|0|17|0|80|
193
194 231 Alessio Valeri
#### STATUS UPDATE MESSAGE
195 1 Alessio Valeri
196 231 Alessio Valeri
**The following 48Byte seems to be a periodic status update message**
197 247 Alessio Valeri
The parameter are in the same order as the table above: 1) MODE, 2)PUMP, 3) WATER SET TEMP, ETC ..
198 259 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | - | - | | MODE | PUMP?? | WATER SET TEMP CYCLE1 | WATER SET TEMP CYCLE2 | DHW SET TEMP | POOL SET TEMP | ERROR CODE | | | ROOM 1 SET TEMP | | | | | | | | ROOM ENABLE | | | UNK1 | UNK2 | | | | | | |  | |  |  | | | | | | CRC | 
199 107 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
200 1 Alessio Valeri
|146|0|48|1|1|1|0|97|62|0|8|0| **11** |12|45|24|0|0|0|26|28|28|28|28|28|28|28|0|0|0|0|160|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|242|
201
202 208 Alessio Valeri
**MODE** : 4/5(AUTO), 8/9(COOL), 64/65(HEAT)
203
**PUMP** : 16 ENABLED ?
204
**ROOM ENABLE** : 1(ROOM 1),
205
**UNK1** : SEEN VALUES: 0,128
206 209 Alessio Valeri
**UNK2** : SEEN VALUES: 32,160,224 ( SEE FOLLOWING TABLE )
207 208 Alessio Valeri
208
|7 |6 |5 |4 |3 |2 |1 |0 |
209
|--|--|--|--|--|--|--|--|
210
| WP ECO MODE HEAT | WP ECO MODE COOL  | 1 | 0 | 0 | 0 | 0 | 0 |
211
212
213 209 Alessio Valeri
**ERROR CODE** : SEEN VALUES: A1,A5
214 19 Alessio Valeri
215 182 Alessio Valeri
### ADDRESS 50 ( ~~HI-MIT INTERFACE~~ IDU )
216 207 Alessio Valeri
| SRC | CTRL |LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | CRC |
217 95 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
218 1 Alessio Valeri
|50|0|9|1|1|1|0|240|248|
219 95 Alessio Valeri
220 207 Alessio Valeri
| SRC | CTRL |LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | CRC |
221 95 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
222 42 Alessio Valeri
|50|0|9|1|1|1|255|241|6|
223
224 101 Alessio Valeri
225 185 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR |- | DSW8 ADDR |- |- |- | MODE | PUMP ? | WATER SET TEMP | ? | IDU GAS TEMPERATURE |- | IDU LIQUID TEMPERATURE | ~~WATER OUT PHEX TEMP~~ NOT SURE | WATER INLET TEMP | | | | | | | | |  | CRC |
226 101 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
227 1 Alessio Valeri
|50|0|28|1|1|1|0|255|24|32| *0* |22|24| **16** |129|20| **11** |12|0|0|22|0|62|0|6|0|2|122|
228 128 Alessio Valeri
229 129 Alessio Valeri
MODE is 32 when CYCLE 1 is OFF, when COOL MODE on CYCLE1 is enabled it changes to 9.
230 130 Alessio Valeri
PUMP ? becomes 1 when cooling is enabled. Change to 17 when water pump is running. <- **EDIT: NOT 100% SURE** (PUMP SEEMS TO RUN EVEN WHEN PUMP=1 , MAYBE 1->CYCLE 1 ENABLED AND 17-> CYCLE1&ROOM1 ENABLED)
231 129 Alessio Valeri
WATER SET TEMP IS SET WHEN CYCLE 1 IS ENABLED
232 23 Alessio Valeri
233 174 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | TEMP? | | | | | | | | | | | | | | | | | | | | | | | CRC | 
234 113 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
235 43 Alessio Valeri
|50|0|32|1|1|1|0|159|30|129|129|20|60|0|7|129|30|26|100|3|0|0|0|0|0|0|0|0|0|2|0|111|
236
237 23 Alessio Valeri
### ADDRESS 35 (UNKNOWN)
238 27 Alessio Valeri
239 172 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | CRC |
240 96 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
241
|35|0|10|1|0|1|255|15|20|238|
242 1 Alessio Valeri
243 172 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | | | |  | CRC |
244 96 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
245
|35|0|14|1|0|1|1|254|16|32|16|32|0|241|
246 1 Alessio Valeri
247 190 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | | | EVAP GAS TEMP | | DISCHARGER TEMPERATURE | | ~~IDU LIQUID TEMP~~ | | FREQUENCE | CURRENT | EVO% | | | | | | |  | CRC |
248 96 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
249 26 Alessio Valeri
|35|0|28|1|0|1|255|242|3|22|128| **25** |0| **51** |128| **17** |110|0|0|0|41|41|1|3|241|208|0|114|
250
251 114 Alessio Valeri
252
253 190 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | | | | | | | | | OUTDOOR TEMP | | EVAP GAS TEMP | | DISCHARGER TEMPERATURE |  | ~~IDU LIQUID TEMP~~ | | FREQUENCE | CURRENT | EVO% | | | | | | | | CRC | 
254 114 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
255
|35|0|36|1|0|1|1|255|0|40|32|0|0|0|2|0|3|20|128| **22** |0| **42** |128| **14**| 100|0|0|0|41|41|1|3|241|208|0|178|
256 115 Alessio Valeri
257 32 Alessio Valeri
Message similar to the previous one with added 8 byte.
258
259 168 Alessio Valeri
|35|240|8|9|224|9|255|231| -> SENT WHEN THERE IS NO COMMUNICATION WITH OUDOOR UNIT ? LOOKS LIKE A DISCOVERY MESSAGE
260
261 158 Alessio Valeri
### ADDRESS 47 ( HI-MIT INTERFACE )
262 78 Alessio Valeri
263 1 Alessio Valeri
Unit 47 seems to send only this request that 242 replies to
264 79 Alessio Valeri
265 171 Alessio Valeri
|SRC | CTRL | LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? | ? | CRC |
266 100 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
267 1 Alessio Valeri
|47|0|10|202|160|1|1|108|0|12|
268 160 Alessio Valeri
269
### ADDRESS 57 ( HI-MIT INTERFACE )
270
271
This message is seen during device discovery
272
273 165 Alessio Valeri
|SRC | CTRL | LEN | - | DSW1 ADDR | ? | ? | ? | ? | CRC |
274 1 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
275 161 Alessio Valeri
|57|3|10|202|160|255|255|0|0|99|
276 36 Alessio Valeri
277 159 Alessio Valeri
### ADDRESS 63 ( HI-MIT INTERFACE )
278 81 Alessio Valeri
Unit 63 seems to only send request that 243 replies to. No other messages are captured at this time.
279
280 169 Alessio Valeri
|SRC | CTRL |LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? |CRC |
281 98 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
282
|63|1|9|202|160|1|0|0|99|
283
284 169 Alessio Valeri
|SRC | CTRL |LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? |CRC |
285 98 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
286
|63|1|9|202|160|1|0|1|98|
287 41 Alessio Valeri
288 199 Alessio Valeri
### ADDRESS 242 (UNKNOWN)
289
290 204 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | |WATER TEMP | | | ROOM1 TEMP ? |  | | | | | | | ROOM1 SET TEMP | | | | | | | | | | | | | | | | | WATER PUMP SPEED | | WATER FLOW (1 digit) |  | | | | | | CRC | 
291 199 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
292
|242|0|48|1|1|1|1|108|62|0| **7** |129|129|27|0|0|0|0|0|0|0|22|0|0|0|0|0|0|0|20|60|50|20|24|12|129|129|0| **14** |3| **14** |0|24|2|4|1|1|111|
293
294 41 Alessio Valeri
### ADDRESS 243 (UNKNOWN)
295 1 Alessio Valeri
Unit 243 seems to reply to 63 requests.
296 187 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR  | | | | | | | | | | | | | | | FREQUENCY | | TARGET FREQUENCY | | OUTDOOR TEMP | | | | | | | DISCHARGER TEMP | | | | | | | | |  | | FREQUENCE | | | EVAP GAS TEMP | | | | CRC | 
297 99 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
298
|243|1|48|1|0|0|255|192|6|0|0|2|0|0|0|0|0|0|0|0|0|64|30|17|159|0|0|60|20|30|0|1|30|0|145|0|0|0|0|34|0|24|0|29|0|0|0|68|
299 1 Alessio Valeri
300 206 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | | | | | | | | | | | FREQUENCE |  | | | | | | | | | | | |  | WATER PUMP SPEED? | | | | | | | | |  | |  | WATER FLOW? | | | | | | CRC | 
301 99 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
302
|243|1|48|1|0|0|255|193|6|0|0|0|0|26|0|0|0|0|7|0|0|0|129|0|0|0|29|0|0|100|29|0|0|0|0|3|129|0|0|0|0|0|129|0|0|0|0|243|