Alessio Valeri, 08/14/2025 03:29 AM

1 1 Alessio Valeri
# Messages
2 70 Alessio Valeri
3
Observing the traffic on the bus we can see there are different units. These are the address found on the 12 bus : 
4 21 Alessio Valeri
5 71 Alessio Valeri
|ADDRESS|UNIT |
6
|--|--|
7 72 Alessio Valeri
| 41 | Hi-Mit remote controller  |
8 1 Alessio Valeri
| 47 | Hi-Mit remote controller |
9 220 Alessio Valeri
| 50 | Indoor Unit |
10 151 Alessio Valeri
| 57 | Hi-Mit remote controller |
11 1 Alessio Valeri
| 63 | Hi-Mit remote controller |
12 150 Alessio Valeri
| 34 |  |
13 220 Alessio Valeri
| 35 | Outodoor Unit |
14 219 Alessio Valeri
| 146 | Indoor Unit |
15 150 Alessio Valeri
| 242 |  |
16
| 243 |  |
17
18 51 Alessio Valeri
# REQUESTS / REPLIES ANALYSIS
19 52 Alessio Valeri
 Here I try to report any communication pattern I can find :
20 1 Alessio Valeri
21 67 Alessio Valeri
## 41 - 146 interaction
22
Messages exchanged between Hi-mit interface and outdoor unit
23
WIP
24
25 52 Alessio Valeri
## 47 - 242 interaction
26 60 Alessio Valeri
<span style="color:darkorange">|47|0|10|202|160|1|1|108|0|12|</span>
27 52 Alessio Valeri
<span style="color:green">ACK from 242</span>
28
|242|0|48|1|1|1|1|108|62|0|31|129|129|27|0|0|0|0|0|0|0|22|0|0|0|0|0|0|0|20|60|50|7|24|25|129|129|0|100|3|0|0|8|0|4|0|0|7|
29
<span style="color:green">ACK from 47</span>
30
31 53 Alessio Valeri
## 50 - 35 interaction
32
33 57 Alessio Valeri
<span style="color:darkorange">|50|0|9|1|1|1|0|240|248|</span>
34 1 Alessio Valeri
<span style="color:green">ACK from 35</span>
35 59 Alessio Valeri
|35|0|36|1|0|1|1|255|0|40|32|0|0|0|2|0|3|34|128|31|0|31|128|18|170|0|0|0|41|41|1|3|241|208|0|106|
36 54 Alessio Valeri
<span style="color:green">ACK from 50</span>
37 57 Alessio Valeri
<span style="color: darkorange">|50|0|28|1|1|1|0|255|24|32|0|7|24|33|129|34|30|30|0|0|25|0|62|0|6|0|2|100|</span>
38 54 Alessio Valeri
<span style="color:green">ACK from 35</span>
39 59 Alessio Valeri
|35|0|14|1|0|1|1|254|16|32|16|32|0|241|
40 54 Alessio Valeri
<span style="color:green">ACK from 50</span>
41 57 Alessio Valeri
<span style="color: darkorange">|50|0|32|1|1|1|0|159|31|129|129|20|60|0|7|129|31|26|100|3|0|0|0|0|0|0|0|0|0|2|0|111|</span>
42 53 Alessio Valeri
<span style="color:green">ACK from 35</span>
43
44 1 Alessio Valeri
## 63 - 243 interaction
45 52 Alessio Valeri
46 61 Alessio Valeri
<span style="color:darkorange">|63|1|9|202|160|1|0|0|99|</span>
47 50 Alessio Valeri
<span style="color:green">ACK from 243</span>
48 45 Alessio Valeri
|243|1|48|1|0|0|255|192|6|0|0|2|0|0|0|0|0|0|0|0|0|66|34|18|178|0|0|60|20|31|0|9|31|0|145|0|0|0|0|33|0|24|0|30|0|0|0|92|
49 61 Alessio Valeri
<span style="color:darkorange">|63|1|9|202|160|1|0|1|98|</span>
50 50 Alessio Valeri
<span style="color:green">ACK from 243</span>
51 45 Alessio Valeri
|243|1|48|1|0|0|255|193|6|0|0|0|0|26|0|0|0|0|7|0|0|0|129|0|0|0|31|0|0|100|31|0|0|0|0|3|129|0|0|0|0|0|129|0|0|0|0|243|
52 1 Alessio Valeri
53 152 Alessio Valeri
## DEVICE DISCOVERY
54 154 Alessio Valeri
When the Hi-mit interface is looking for devices on H-LINK bus the following messages are sent: (This messages were logged with **no device connected**  on H-LINK bus)
55 152 Alessio Valeri
56 167 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR| | | |CRC |
57 152 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
58 153 Alessio Valeri
|41|0|9|202|160|255|255|241|146|
59 1 Alessio Valeri
60 167 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR  | | | |  |CRC |
61 153 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
62 155 Alessio Valeri
|57|3|10|202|160|255|255|0|0|99|
63 152 Alessio Valeri
64 65 Alessio Valeri
## AUTODISCOVERY ??
65 73 Alessio Valeri
From time to time these messages appears on the bus, they are not always grouped together and they are not acknowledged, maybe they are used to report their presence ?
66 65 Alessio Valeri
67 85 Alessio Valeri
68 90 Alessio Valeri
|35|0|10|1|0|1|255|15|20|238| <- UPDATE: VALUE 15 & 20 CHANGE OVER TIME, ARE THEY TEMPERATURE ?
69 65 Alessio Valeri
|50|0|9|1|1|1|255|241|6|
70 1 Alessio Valeri
|41|0|9|202|160|255|255|241|146|
71 86 Alessio Valeri
72
|35|0|28|1|0|1|255|242|3|34|128|31|0|31|128|18|170|0|0|0|41|41|1|3|241|208|0|171| -> This is a status update but it seems no one requests or acknowledge
73 45 Alessio Valeri
74 62 Alessio Valeri
## ALL MESSAGES
75 75 Alessio Valeri
Here are reported all the messages captured :
76 45 Alessio Valeri
77 177 Alessio Valeri
Note: DSW8 ADDR field is the binary encoded value +1
78
Example: 
79
![](clipboard-202508070058-zy4vb.png)
80
In the image above DSW8 ADDR is equal to 8+1 = **9**
81
82
DSW1 field is thebynary encoded value set on the Hi-mit interface
83
84
85 11 Alessio Valeri
### ADDRESS 41 ( HI-MIT INTERFACE )
86 163 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR | | | |CRC |
87 91 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
88 1 Alessio Valeri
|41|0|9|202|160|255|255|241|146|
89 92 Alessio Valeri
90 176 Alessio Valeri
| SRC | CTRL |LEN | | DSW1 ADDR | DSW8 ADDR | | |CRC |
91 92 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
92 1 Alessio Valeri
|41|0|9|202|160|1|1|97|2|
93 2 Alessio Valeri
94 163 Alessio Valeri
| SRC | CTRL | LEN | | DSW1 ADDR | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | |  | |  | | | | | CRC | 
95 91 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
96 4 Alessio Valeri
|41|0|48|202|160|1|1|107|62|31|8|255|11|12|45|24|0|0|26|28|28|28|28|28|28|28|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|211|
97 92 Alessio Valeri
98 163 Alessio Valeri
| SRC | CTRL | LEN | | DSW1 ADDR | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | | CRC | 
99 92 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
100 1 Alessio Valeri
|41|0|48|202|160|1|1|107|62|0|8|0|11|12|45|24|0|0|26|28|28|28|28|28|28|28|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|51|
101 5 Alessio Valeri
102 237 Alessio Valeri
## Address 146
103 108 Alessio Valeri
Messages coming from 146 seems to be associated with the master controller status.
104 1 Alessio Valeri
105 210 Alessio Valeri
**The following message is sent when there is a parameter change on MASTER CONTROLLER:**
106
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | PARAMETER ID | SET VALUE | CRC |
107
|--|--|--|--|--|--|--|--|--|--|--|--|
108 226 Alessio Valeri
|146|0|12|1|1|1|0| 99 |62| **x** | **x** | xx |
109 1 Alessio Valeri
110 226 Alessio Valeri
Multiple parameters can be concatenated in a request  in the following way: 
111
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | PARAMETER ID x1 | SET VALUE x1 |PARAMETER ID x2 | SET VALUE x2 |PARAMETER ID xn | SET VALUE xn | CRC |
112 227 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
113 228 Alessio Valeri
|146|0| 10+(n*2) |1|1|1|0| 99 |62| xx | xx |xx| xx |xx | xx | xx |
114 215 Alessio Valeri
115 229 Alessio Valeri
#### PARAMETERS ID
116
These are the parameters ID :
117 210 Alessio Valeri
| DESCRIPTION |PARAMETER ID |
118
|--|--|
119 216 Alessio Valeri
| **MODE**              | 1 |
120 243 Alessio Valeri
| CYCLE MODE?           | 2 |
121 216 Alessio Valeri
| **CYCLE1 WATER TEMP** | 3 |
122
| **CYCLE2 WATER TEMP** | 4 |
123
| **DHW SET TEMP**      | 5 |
124
| **POOL SET TEMP**     | 6 |
125 252 Alessio Valeri
| **ERROR CODE**     | 7 |
126 260 Alessio Valeri
| ?     | 8 |
127 221 Alessio Valeri
| ?     | 9 |
128 216 Alessio Valeri
| **ROOM1 SET TEMP**    | 10 |
129 215 Alessio Valeri
| UNKNOWN TEMP          | 11 |
130
| UNKNOWN TEMP          | 12 |
131
| UNKNOWN TEMP          | 13 |
132
| UNKNOWN TEMP          | 14 |
133
| UNKNOWN TEMP          | 15 |
134
| UNKNOWN TEMP          | 16 |
135 240 Alessio Valeri
| UNKNOWN TEMP          | 17 |
136
| **ROOM ENABLE**       | 18 |
137 241 Alessio Valeri
| **ROOM ECO MODE?**       | 19 |
138 245 Alessio Valeri
| DHW CONFIG ?           | 20 |
139 217 Alessio Valeri
| UNKNOWN            | 21 |
140 223 Alessio Valeri
| WATER PUMP CONFIG?        | 22 |
141 215 Alessio Valeri
142
#### MODE
143 253 Alessio Valeri
144
| BIT 7 | BIT 6  | BIT 5 | BIT 4 | BIT 3 | BIT 2 |  BIT 1| BIT 0 |
145
|--|--|--|--|--|--|--|--|
146 257 Alessio Valeri
| | HEAT MODE |  |  | COOL MODE | AUTO MODE | CYCLE 2 ENABLE | CYCLE1 ENABLE |
147 253 Alessio Valeri
148 257 Alessio Valeri
This parameter sets the working mode of the unit: HEAT / COOL / AUTO. Only one of the 3 mode can be active at a single time.
149 215 Alessio Valeri
When there is a change of the working mode on the master controller also the following parameters are updated in a single request.
150 1 Alessio Valeri
3,4,10,11,12,13,14,15,16,17
151
152 230 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | - | MODE: | VALUE | CYCLE1 SET TEMP: | VALUE | CYCLE2 SET TEMP: | VALUE | ROOM1 SET TEMP: | VALUE  | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | ROOM? SET TEMP: | VALUE | CRC |
153 225 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
154 224 Alessio Valeri
|146|0|32|9|1|9|0|99|62|1|8|3|6|4|12|10|23|11|28|12|28|13|28|14|28|15|28|16|28|17|28|115|
155
156 246 Alessio Valeri
#### CYCLE MODE: 16 (CYCLE1 ECO MODE OFF),17 (CYCLE1 ECO MODE ON)
157 248 Alessio Valeri
158 249 Alessio Valeri
| BIT 7 | BIT 6  | BIT 5 | BIT 4 | BIT 3 | BIT 2 |  BIT 1| BIT 0 |
159 248 Alessio Valeri
|--|--|--|--|--|--|--|--|
160 261 Alessio Valeri
|? | ? | ? |  PUMP ENABLE | ? | ? |CYCLE2 ECO MODE| CYCLE1 ECO MODE |
161 248 Alessio Valeri
162 246 Alessio Valeri
#### DHW CONFIG: 0 DHW BOOST OFF, 128 DHW BOOST ON
163 213 Alessio Valeri
164 212 Alessio Valeri
**EXAMPLE:** The following message is sent when the MASTER CONTROLLER POOL water set temp is changed to 27°C :
165 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | POOL WATER TEMP | SET TEMP | CRC |
166 135 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
167 139 Alessio Valeri
|146|0|12|1|1|1|0| 99 |62| **6** | **27** |77| 
168
169
170 1 Alessio Valeri
The following message is sent when the MASTER CONTROLLER **POOL** OR **DHW** is changed to **DISABLED** :
171 222 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | POOL/DHW| SET VALUE | CRC |
172 139 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
173
|146|0|12|1|1|1|0| 99 |62| **7** | **0** |87|  
174 141 Alessio Valeri
175
176 143 Alessio Valeri
ALSO THE FOLLOWING MESSAGE:
177
|146|0|43|1|1|1|0|96|62|0|0|73|119|185|131|9|0|0|16|2|64|1|0|24|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|50|
178
179 139 Alessio Valeri
 
180 1 Alessio Valeri
181 139 Alessio Valeri
**The following message is sent when the MASTER CONTROLLER POOL is changed to ENABLED :**
182 222 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | POOL/DHW | SET VALUE | CRC |
183 139 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
184 142 Alessio Valeri
|146|0|12|1|1|1|0| 99 |62| **7** | **162** |145| 
185 1 Alessio Valeri
186 142 Alessio Valeri
ALSO THE FOLLOWING MESSAGE:
187
|146|0|43|1|1|1|0|96|62|0|0|73|119|185|131|9|0|0|16|130|64|1|0|24|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|178|
188 1 Alessio Valeri
189
190 142 Alessio Valeri
191 140 Alessio Valeri
**The following message is sent when the MASTER CONTROLLER DHW is changed to ENABLED :**
192 222 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | POOL/DHW | SET VALUE | CRC |
193 1 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
194 142 Alessio Valeri
|146|0|12|1|1|1|0| 99 |62| **7** | **22** |65|
195
196
ALSO THE FOLLOWING MESSAGE:
197
|146|0|43|1|1|1|0|96|62|0|0|73|119|185|131|9|0|0|16|34|64|1|0|24|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|18|
198
199 13 Alessio Valeri
200
201 14 Alessio Valeri
**Inviato quando seleziono la modalità HEAT**
202 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | MODE ?  |  | |  | | |  | | | | | | | | | | |  | | CRC |
203 104 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
204 16 Alessio Valeri
|146|0|30|1|1|1|0|99|62|1| **64** |3|20|4|20|11|22|12|22|13|22|14|22|15|22|16|22|17|22|24|
205 104 Alessio Valeri
206 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | | CRC |
207 105 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
208 14 Alessio Valeri
|146|0|12|1|1|1|0|99|62|22|128|198|
209
210
**Inviato quando seleziono la modalità COLD**
211 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | MODE ?  |  | |  | | |  | | | | | | | | | | |  | | CRC |
212 104 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
213 16 Alessio Valeri
|146|0|30|1|1|1|0|99|62|1| **8** |3|13|4|16|11|28|12|28|13|28|14|28|15|28|16|28|17|28|71|
214 104 Alessio Valeri
215 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | | | CRC |
216 105 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|
217 14 Alessio Valeri
|146|0|12|1|1|1|0|99|62|22|160|230|
218
219
**Inviato quando seleziono la modalità AUTO**
220 180 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | |  MODE ? |  | |  | | |  | | | | | | | | | |  | CRC |
221 16 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
222 14 Alessio Valeri
|146|0|28|1|1|1|0|99|62|1| **4** |3|28|11|0|12|0|13|0|14|0|15|0|16|0|17|0|80|
223
224 231 Alessio Valeri
#### STATUS UPDATE MESSAGE
225 1 Alessio Valeri
226 231 Alessio Valeri
**The following 48Byte seems to be a periodic status update message**
227 247 Alessio Valeri
The parameter are in the same order as the table above: 1) MODE, 2)PUMP, 3) WATER SET TEMP, ETC ..
228 259 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | - | - | | MODE | PUMP?? | WATER SET TEMP CYCLE1 | WATER SET TEMP CYCLE2 | DHW SET TEMP | POOL SET TEMP | ERROR CODE | | | ROOM 1 SET TEMP | | | | | | | | ROOM ENABLE | | | UNK1 | UNK2 | | | | | | |  | |  |  | | | | | | CRC | 
229 107 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
230 1 Alessio Valeri
|146|0|48|1|1|1|0|97|62|0|8|0| **11** |12|45|24|0|0|0|26|28|28|28|28|28|28|28|0|0|0|0|160|0|0|0|0|0|0|0|0|0|0|0|0|0|0|0|242|
231
232 208 Alessio Valeri
**MODE** : 4/5(AUTO), 8/9(COOL), 64/65(HEAT)
233
**PUMP** : 16 ENABLED ?
234
**ROOM ENABLE** : 1(ROOM 1),
235
**UNK1** : SEEN VALUES: 0,128
236 209 Alessio Valeri
**UNK2** : SEEN VALUES: 32,160,224 ( SEE FOLLOWING TABLE )
237 208 Alessio Valeri
238
|7 |6 |5 |4 |3 |2 |1 |0 |
239
|--|--|--|--|--|--|--|--|
240
| WP ECO MODE HEAT | WP ECO MODE COOL  | 1 | 0 | 0 | 0 | 0 | 0 |
241
242
243 209 Alessio Valeri
**ERROR CODE** : SEEN VALUES: A1,A5
244 19 Alessio Valeri
245 182 Alessio Valeri
### ADDRESS 50 ( ~~HI-MIT INTERFACE~~ IDU )
246 207 Alessio Valeri
| SRC | CTRL |LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | CRC |
247 95 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
248 1 Alessio Valeri
|50|0|9|1|1|1|0|240|248|
249 95 Alessio Valeri
250 207 Alessio Valeri
| SRC | CTRL |LEN | DSW8 ADDR | - | DSW8 ADDR | - | - | CRC |
251 95 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
252 42 Alessio Valeri
|50|0|9|1|1|1|255|241|6|
253
254 101 Alessio Valeri
255 185 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR |- | DSW8 ADDR |- |- |- | MODE | PUMP ? | WATER SET TEMP | ? | IDU GAS TEMPERATURE |- | IDU LIQUID TEMPERATURE | ~~WATER OUT PHEX TEMP~~ NOT SURE | WATER INLET TEMP | | | | | | | | |  | CRC |
256 101 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
257 1 Alessio Valeri
|50|0|28|1|1|1|0|255|24|32| *0* |22|24| **16** |129|20| **11** |12|0|0|22|0|62|0|6|0|2|122|
258 128 Alessio Valeri
259 129 Alessio Valeri
MODE is 32 when CYCLE 1 is OFF, when COOL MODE on CYCLE1 is enabled it changes to 9.
260 130 Alessio Valeri
PUMP ? becomes 1 when cooling is enabled. Change to 17 when water pump is running. <- **EDIT: NOT 100% SURE** (PUMP SEEMS TO RUN EVEN WHEN PUMP=1 , MAYBE 1->CYCLE 1 ENABLED AND 17-> CYCLE1&ROOM1 ENABLED)
261 129 Alessio Valeri
WATER SET TEMP IS SET WHEN CYCLE 1 IS ENABLED
262 23 Alessio Valeri
263 174 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | TEMP? | | | | | | | | | | | | | | | | | | | | | | | CRC | 
264 113 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
265 43 Alessio Valeri
|50|0|32|1|1|1|0|159|30|129|129|20|60|0|7|129|30|26|100|3|0|0|0|0|0|0|0|0|0|2|0|111|
266
267 23 Alessio Valeri
### ADDRESS 35 (UNKNOWN)
268 27 Alessio Valeri
269 172 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | CRC |
270 96 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
271
|35|0|10|1|0|1|255|15|20|238|
272 1 Alessio Valeri
273 172 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | | | |  | CRC |
274 96 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
275
|35|0|14|1|0|1|1|254|16|32|16|32|0|241|
276 1 Alessio Valeri
277 190 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | | | EVAP GAS TEMP | | DISCHARGER TEMPERATURE | | ~~IDU LIQUID TEMP~~ | | FREQUENCE | CURRENT | EVO% | | | | | | |  | CRC |
278 96 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
279 26 Alessio Valeri
|35|0|28|1|0|1|255|242|3|22|128| **25** |0| **51** |128| **17** |110|0|0|0|41|41|1|3|241|208|0|114|
280
281 114 Alessio Valeri
282
283 190 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | DSW8 ADDR | | | | | | | | | | | | OUTDOOR TEMP | | EVAP GAS TEMP | | DISCHARGER TEMPERATURE |  | ~~IDU LIQUID TEMP~~ | | FREQUENCE | CURRENT | EVO% | | | | | | | | CRC | 
284 114 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
285
|35|0|36|1|0|1|1|255|0|40|32|0|0|0|2|0|3|20|128| **22** |0| **42** |128| **14**| 100|0|0|0|41|41|1|3|241|208|0|178|
286 115 Alessio Valeri
287 32 Alessio Valeri
Message similar to the previous one with added 8 byte.
288
289 168 Alessio Valeri
|35|240|8|9|224|9|255|231| -> SENT WHEN THERE IS NO COMMUNICATION WITH OUDOOR UNIT ? LOOKS LIKE A DISCOVERY MESSAGE
290
291 158 Alessio Valeri
### ADDRESS 47 ( HI-MIT INTERFACE )
292 78 Alessio Valeri
293 1 Alessio Valeri
Unit 47 seems to send only this request that 242 replies to
294 79 Alessio Valeri
295 171 Alessio Valeri
|SRC | CTRL | LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? | ? | CRC |
296 100 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
297 1 Alessio Valeri
|47|0|10|202|160|1|1|108|0|12|
298 160 Alessio Valeri
299
### ADDRESS 57 ( HI-MIT INTERFACE )
300
301
This message is seen during device discovery
302
303 165 Alessio Valeri
|SRC | CTRL | LEN | - | DSW1 ADDR | ? | ? | ? | ? | CRC |
304 1 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|
305 161 Alessio Valeri
|57|3|10|202|160|255|255|0|0|99|
306 36 Alessio Valeri
307 159 Alessio Valeri
### ADDRESS 63 ( HI-MIT INTERFACE )
308 81 Alessio Valeri
Unit 63 seems to only send request that 243 replies to. No other messages are captured at this time.
309
310 169 Alessio Valeri
|SRC | CTRL |LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? |CRC |
311 98 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
312
|63|1|9|202|160|1|0|0|99|
313
314 169 Alessio Valeri
|SRC | CTRL |LEN | - | DSW1 ADDR | DSW8 ADDR | ? | ? |CRC |
315 98 Alessio Valeri
|--|--|--|--|--|--|--|--|--|
316
|63|1|9|202|160|1|0|1|98|
317 41 Alessio Valeri
318 199 Alessio Valeri
### ADDRESS 242 (UNKNOWN)
319
320 204 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | - | DSW8 ADDR | | | | |WATER TEMP | | | ROOM1 TEMP ? |  | | | | | | | ROOM1 SET TEMP | | | | | | | | | | | | | | | | | WATER PUMP SPEED | | WATER FLOW (1 digit) |  | | | | | | CRC | 
321 199 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
322
|242|0|48|1|1|1|1|108|62|0| **7** |129|129|27|0|0|0|0|0|0|0|22|0|0|0|0|0|0|0|20|60|50|20|24|12|129|129|0| **14** |3| **14** |0|24|2|4|1|1|111|
323
324 41 Alessio Valeri
### ADDRESS 243 (UNKNOWN)
325 1 Alessio Valeri
Unit 243 seems to reply to 63 requests.
326 187 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR  | | | | | | | | | | | | | | | FREQUENCY | | TARGET FREQUENCY | | OUTDOOR TEMP | | | | | | | DISCHARGER TEMP | | | | | | | | |  | | FREQUENCE | | | EVAP GAS TEMP | | | | CRC | 
327 99 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
328
|243|1|48|1|0|0|255|192|6|0|0|2|0|0|0|0|0|0|0|0|0|64|30|17|159|0|0|60|20|30|0|1|30|0|145|0|0|0|0|34|0|24|0|29|0|0|0|68|
329 1 Alessio Valeri
330 206 Alessio Valeri
|SRC | CTRL | LEN | DSW8 ADDR | | | | | | | | | | | | FREQUENCE |  | | | | | | | | | | | |  | WATER PUMP SPEED? | | | | | | | | |  | |  | WATER FLOW? | | | | | | CRC | 
331 99 Alessio Valeri
|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|--|
332
|243|1|48|1|0|0|255|193|6|0|0|0|0|26|0|0|0|0|7|0|0|0|129|0|0|0|29|0|0|100|29|0|0|0|0|3|129|0|0|0|0|0|129|0|0|0|0|243|